motorni napisal/-a:PogachnyK napisal/-a:Če je namenjen prezračevanju vnetljivh hlapov, mora imeti tako nalepkico
Ni res.
Taka nalepka je predpisana v pravilniku o protieksplozijski zaščiti. Ta pa ne velja za plovila.
Res je, kar si napisal, ampak kaj ni smisel, da ti ventilator prepreči nastanek explozije, kot pa da je ventilator vir vžiga?
Sr290 mogoče malo za orientacijo kakšna beseda o standardih, ki se nanašajo na požarno varnost na plovilih
mall craft -- Fire protection -- Part 1: Craft with a hull length of up to and including 15 m
Točka 7 pa pravi
7 Fixed fire-extinguishing systems
7.1 Purpose This clause specifies requirements for fixed fire-fighting systems, manually or automatically put into operation, if fitted, using extinguishing media suitable for total coverage or flooding of an enclosed space and capable of extinguishing fires of Class A and B. These requirements are relative to size, location and installation.
This part of ISO 9094 does not specify the technical requirements for the cylinders themselves which may be subject to national regulations.
7.2 Requirements
7.2.1 Manual system
A fixed system put into operation manually shall be activated from the main steering position.
If that position is more than 5 m away from the section or space to be protected, a means of local activation shall be provided near that space.
7.2.2 Automatic system
A fixed system that is automatically activated shall comply with the requirements of 7.4.
7.2.3 Manual/automatic combined system
The arrangement of a combined manual/automatic system shall be such that the operator can manually override the automatic mode. The system shall comply with the requirements of 7.4.
7.3 Application The installation of a fixed system using an asphyxiant as the extinguishing medium is limited to spaces in a boat that are not intended for accommodation purposes and are separated from the accommodation area. This requirement is fulfilled if the spaces have no permanent openings other than for the following purposes: connection to the surrounding bilges; ventilation of engine space and supply of combustion air; openings for piping and cables; openings for access to equipment.
7KLVGRFXPHQWLVSHUVRQDOL]HGIRU^3XEOLF5HVRXUFH,QF`2UGHU^`3XUFKDVHG^`
ISO 9094-1:2003(E)
12 © ISO 2003 – All rights reserved
If the extinguishing medium is an asphyxiant, the separating structure shall be constructed to minimize the flow of the medium into the accommodation area.
7.4 Installation
7.4.1 General
The components of a fixed system shall be securely fastened to the boat's structure to withstand motions, shock and vibrations during normal running conditions.
Cylinders, distribution lines and controls shall be located so that they will not be subject to temperatures outside the system's designed operating range, while the boat is in service.
7.4.2 Cylinders/containers
Cylinders/containers may be installed either inside or outside the space to be protected.
To minimize corrosion, cylinders shall be mounted clear of the anticipated bilge-water level. They shall be accessible for removal, and the controls and dials shall be readily accessible and visible. Cylinders shall be mounted to provide clearance above surfaces on which water may accumulate.
7.4.3 Manual system, release device The release device shall be visible or its location visibly labelled and the protected space identified.
The release device shall be readily accessible and operable.
7.4.4 Distribution line
Non-metallic components of the distribution line(s), including fixtures that are not intended to melt as part of the fire-fighting system as installed, shall be fire resistant in accordance with ISO 7840.
Solder or brazing material used for metallic lines or fittings shall have a melting temperature of not less than 600 °C.
The number and location of discharge nozzle(s) shall ensure effective extinguishing of fires within the space.
7.5 Discharge and control 7.5.1 A visual indication of discharge shall be provided. 7.5.2 The system shall be installed such that the discharge shall be completed according to the extinguisher manufacturer's specification. 7.5.3 If the extinguishing medium is an asphyxiant and if the protected space is of sufficient size to be occupied by a person (working or carrying out another action), upon activating the system an alarm, which is audible throughout the craft, shall sound prior to the extinguishing medium being released. 7.5.4 If more than one system is installed in a hazard space, each system shall be capable of individually protecting the space, unless they are simultaneously discharged.
7.6 Operation
7.6.1 Range of operation
The fixed system shall be capable of operating above an ambient temperature of 0 °C.
ISO 9094-1:2003(E)
© ISO 2003 – All rights reserved 13
7.6.2 Discharge instructions A label showing how to discharge the system shall be provided immediately adjacent to the release device.
7.6.3 Operating instructions
Operating instructions shall be provided for each system. If the extinguishing medium is an asphyxiant, these shall include directions on how to ventilate the space prior to entering for damage assessment and subsequent restarting of the engine.
7.7 Design concentration The extinguishing capacity of the system shall be based on the net volume of the compartment (volume of air plus 20 ).
Imam še en članek o stacionarnih sistemih aktivne požarne zaščite na plovilih:
https://www.dropbox.com/s/wi70e632xnze3vz/fire.pdf?dl=0
In mogoče še enega o požarih na plovilih na splošno:
https://www.dropbox.com/s/20yo5kgcrv8na ... E.pdf?dl=0
cena takšnega enostavnega sistema za gašenje niti ni pretirana, kakšnih certifikatov za lastno uporabo ne potrebuješ. je kar nekaj podjetij v Sloveniji, ki se ukvarjajo s temi zadevami in bi ti verjetno rade volje prodali potrebne elemente. Trenutno s kolegi razvijamo nekaj podobnega, le da bo prvinsko namenjeno uporabi v avtomobilih, vendar pa ne bo noben problem prilagoditi za navtiko, verjetno bo potrebno certificiranje, kar pomeni le še nekaj dodatnih stroškov.